Qtester 104 uses the IEC 60870-5-104. This protocol isn't supported by Plcsim+Nettoplcsim. Even real S7 plc's don't support this protocol without additional hard- and software.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hi,
I think nettoplcsim is working,
But if i try to connect with QTester 104 ->
TCP connected
T<--006: 68 04 07 00 00 00
STARTDTACT
SocketError:1
TCP Disconnect
So i think nettoplcsim is working.
Bun now I'm not shure what the problem is.
Is it nettoplcsim or ist it PLCSIM self?
Sorry for my english and thanks for help :-)
The Log is empty, maybe no connection? :-/
Hi,
Qtester 104 uses the IEC 60870-5-104. This protocol isn't supported by Plcsim+Nettoplcsim. Even real S7 plc's don't support this protocol without additional hard- and software.
Oh, ok PLCSIM doesn't support... okey =(
But S7-1500 work with IEC104 :-)
Ok thanks for you help!
If it's done in software in the S7-1500, maybe it works with Plcsim Advanced, which supports also TCP connections.
Hi Thomas, thanks!!! It is working! Without nettoplcsim, but with plcsim advance :-)
But anyway thanks for your work!